If I have a 100 Amp panelboard with a MCB, can I also put a 100 Amp branch breaker in this panel to feed a 100 amp MLO sub-panel?
Thanks
Thanks
The one I am most familiar with on that max size being less than the panel rating is those 6 and 8 space QO loadcenters with a horizontal bus. The bus is rated 100 amps but they are only rated for 70 amp max breakers to plug onto them. Then of course most 200 amp loadcenters are limited to 100 or 125 amp branches, with exception being use of larger breakers that take more than one space per pole.As long as it's not prohibited by the manufacturer.
(some loadcenters have a max size branch)