Recently I bought a 100 yr old house in Floyd County Va. It has a 100A /240V main breaker panel that is wired on the branch circuits with copper wire, the wire size and breaker sizes are not correct so I'm fixing those. The problem I have is the feed from the main outside is an XHHW-2 AL cable, the two insulated conductors going to the main breaker and the sheild wire that incloses the conductors wound into a uninsulated wire and run to the neut. buss bar. A seperate #8 ground wire run to the neut buss and the buss is bonded to the panel. Please correct me if I'm wrong, the neut conductor should be a covered conductor and the shield wire should be used as a gound conductor, the wire size is to small for a 100 A service. The feed runs under the house so a cable would be best to replace it.
What would be the correct type and size of cable to use.
Thanks so much for helping!