#1 I am trouble shooting a 240/120 panel in a parking structure. This panel feeds HID lighting. The top half of the panel is always on The bottom is fed through a contactor that intercepts the buss. The contactor is operated by a timeclock. The main breaker is an ITE ED43B100 w/ an accessory ground fault relay. The main would trip frequently (1-3 days). I disconnected the G.F. relay and the main has not tripped since, that was about 2 weeks ago. Is there a way to test the relay to see if it is working properly?
#2 On the above install all three phase conductors and the neutral go through the doughnut. How does this sense current? Shouldn't all the phase currents cancel each other?
Hale
#2 On the above install all three phase conductors and the neutral go through the doughnut. How does this sense current? Shouldn't all the phase currents cancel each other?
Hale