100 amp minimum

Status
Not open for further replies.
J

jonny1982

Guest
There is a plaza in PA that some spaces are being redone. There is a small room that isn't rented out as anything yet and the building owner said to put a 50 amp sub panel for the space, said should be good enough. I was then told that a panel for a tenant space, no matter how small the space is, has to be at least 100 amps. Does this sound right. It seems to me that I should be able to put a little 50 amp sub there.

Thanks
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Barring some local ordinance (or my memory) there are minimums for services and outside feeder disconnect, but I know of no NEC minimum for a subpanel in the same building.
 