Okay, I am going to sound dumb. But I want to understand the stuff.
I have a 300-amp main panel and a 100-amp sub-panel, which is fed from the main panel. The sub-panel is protected by its own 100-amp breaker located in the main panel.
The 100-amp sub-panel is dedicated to powering park trail lights, pickleball court lights, and tennis court lights.
### Sub-Panel Details:
The 100-amp sub-panel has 30 breaker slots. The current configuration of branch devices is as follows:
#### Branch Devices:
| Quantity | Poles | Trip Rating | Voltage |
|----------|-------|-------------|---------|
| 5 | 2 | 20 A | 208 V (single phase) |
| 3 | 1 | 20 A | 120 V (single phase) |
| 17 | 1 | Spare | — |
#### Main Breaker Device:
| Quantity | Poles | Trip Rating |
|----------|-------|-------------|
| 1 | 3 | 100 A |
---
I understand that the total current draw from all breakers in the main service panel should not exceed 80% of its capacity, per NEC guidelines. For example, a 20-amp breaker can support up to 16 amps of continuous load (80% of its rated capacity).
Question:
Given this understanding, I am confused about how many 20-amp breakers I can install in the sub-panel. Specifically:
1. The sub-panel already has five 20-amp, 208V single phase breakers and three 20-amp, 120V breakers.
2. When I total the amperage ratings, they appear to exceed the sub-panel's 100-amp capacity.
Could you clarify how this works? Does this mean the breakers’ combined ratings (e.g., 5 x 20 amps + 3 x 20 amps) exceed 100 amps, or is this more about the actual current draw on each breaker?
I have to add dedicated circuits for the grill, oven and receptacle (GFCI) as it is outside in park. So, I am calculate how many slots will be left in a 100 amp panel that has 30 slots.
I have a 300-amp main panel and a 100-amp sub-panel, which is fed from the main panel. The sub-panel is protected by its own 100-amp breaker located in the main panel.
The 100-amp sub-panel is dedicated to powering park trail lights, pickleball court lights, and tennis court lights.
### Sub-Panel Details:
The 100-amp sub-panel has 30 breaker slots. The current configuration of branch devices is as follows:
#### Branch Devices:
| Quantity | Poles | Trip Rating | Voltage |
|----------|-------|-------------|---------|
| 5 | 2 | 20 A | 208 V (single phase) |
| 3 | 1 | 20 A | 120 V (single phase) |
| 17 | 1 | Spare | — |
#### Main Breaker Device:
| Quantity | Poles | Trip Rating |
|----------|-------|-------------|
| 1 | 3 | 100 A |
---
I understand that the total current draw from all breakers in the main service panel should not exceed 80% of its capacity, per NEC guidelines. For example, a 20-amp breaker can support up to 16 amps of continuous load (80% of its rated capacity).
Question:
Given this understanding, I am confused about how many 20-amp breakers I can install in the sub-panel. Specifically:
1. The sub-panel already has five 20-amp, 208V single phase breakers and three 20-amp, 120V breakers.
2. When I total the amperage ratings, they appear to exceed the sub-panel's 100-amp capacity.
Could you clarify how this works? Does this mean the breakers’ combined ratings (e.g., 5 x 20 amps + 3 x 20 amps) exceed 100 amps, or is this more about the actual current draw on each breaker?
I have to add dedicated circuits for the grill, oven and receptacle (GFCI) as it is outside in park. So, I am calculate how many slots will be left in a 100 amp panel that has 30 slots.