I went on a service call today for a routine problem. In the process of troubleshooting, I noticed something I have not seen before.
Two separate buildings. The main building is fed with a 400 amp service.
The secondary building has a panel with a 100 amp main breaker, that is fed from the load side of the 400 amp disconnect on the main building. The conduit run is obviously over 100 feet with #3 copper.
This doesn't seem "legal" to me, yet it is a commercial installation (church) so I would think that it had been inspected by the city and approved.
Doesn't an installation like this fall under the 25' tap rule? At the very least, I think they should have put a fused 100 A disconnect for the secondary building next to the 400 A disconnect at the main building.
Two separate buildings. The main building is fed with a 400 amp service.
The secondary building has a panel with a 100 amp main breaker, that is fed from the load side of the 400 amp disconnect on the main building. The conduit run is obviously over 100 feet with #3 copper.
This doesn't seem "legal" to me, yet it is a commercial installation (church) so I would think that it had been inspected by the city and approved.
Doesn't an installation like this fall under the 25' tap rule? At the very least, I think they should have put a fused 100 A disconnect for the secondary building next to the 400 A disconnect at the main building.