Book says 60 degree column minimum wire size for 100 amps SER aluminum must be 1/0?
I've used 2-2-2-4 SER from HD that says right on the spool 100a rated. If the rating is posted, why not use it?
I've used 2-2-2-4 SER from HD that says right on the spool 100a rated. If the rating is posted, why not use it?
Possibly it is a very high temp fixture wire type? That could have a very high NEC ampacity as long as the terminations are OK.There is a lot of wire that has ratings for ampacity that far exceed what the national electrical code allows. If you look close at the ratings it never says anything about it being an NEC rating. I have used some Teflon insulated wire that I think is 20 gauge and it has a rating of 22 amps if I recall correctly. Stuff probably gets downright warm if you actually use it that way.
Was there fine print/disclaimer stating conditions when you can use it at 100 amps?I've used 2-2-2-4 SER from HD that says right on the spool 100a rated. If the rating is posted, why not use it?
Was it copper or al 2-2-2-4? Not seeing how Al 2-2-2-4 could be used on a 100A subpanel unless fed from a 90A breaker.