Stevenfyeager
Senior Member
- Location
- United States, Indiana
- Occupation
- electrical contractor
Only one inspector in my part of the state does not allow #2 AL to power up a 100 amp subpanel. He sites the NEC table with dwelling services allowing # 2, but says a subpanel is not a service so I must use 310.16, which calls for # 1. Everywhere else I work, #2 AL is fine with inspectors. He says a service will not use full capacity and a subpanel may. ( same goes for a subpanel to a detached garage, also requires a #1, he says.) Is this unusual?