Can I feed a 200 amp main 3 phase distribution panel panel from a 100 amp fused disconect using 2 awg?
Yes, if your conductors are copper and you only need 100 amps.
Roger
why would it need to be copper? can't you round up the OCPD size with AL wire?
#2 AL at 75 deg's is only good for 90 amps, a 90 amp breaker or fuse is a standard size, see 240.6 so you can not "round up" using 240.4(B) in the OP's case.
Roger