100 amp to 200 amp
Yes, if your conductors are copper and you only need 100 amps.
Roger
why would it need to be copper? can't you round up the OCPD size with AL wire?
#2 AL at 75 deg's is only good for 90 amps, a 90 amp breaker or fuse is a standard size, see 240.6 so you can not "round up" using 240.4(B) in the OP's case.
Roger