Hi All,
I have a 800A OCPD rated for 100% duty. I sized the equipment ground to 1/0 per Table 250.122 (2008 NEC). A comment came back stating that Table 250.122 is based on OCPD rated for 80% duty, therefore I need to size my ground to 2/0 for a 1000A OCPD. Does anyone know where in the code this is stated?
Thanks.
I have a 800A OCPD rated for 100% duty. I sized the equipment ground to 1/0 per Table 250.122 (2008 NEC). A comment came back stating that Table 250.122 is based on OCPD rated for 80% duty, therefore I need to size my ground to 2/0 for a 1000A OCPD. Does anyone know where in the code this is stated?
Thanks.