100 gallon Propane Tank with in 15' of Pool sub-panel

Status
Not open for further replies.
I've run into a situation on an Install for a pool sub-panel. We installed the panel in a location chosen by the contractor based on where the pool equipment was going to be located. The Pool installer would not install their equipment because they were within 15' of a 100 gallon above ground propane tank and their pool pump would be close to a propane fitting going to an instant hot water heater. I was unaware that the propane tank was going to be installed in the location that it was but that being said my question is. If my sub-panel is 9' away would it be consider a spark source for that propane tank? Would the pool equipment be considered a spark source next to the propane fitting? The GC moved all the equipment but in the future I would like to have a solid answer for electrical equipment near propane tanks and connections.

Thank you for your thoughts and code knowledge.
 
Some pool equipment actually uses the propane to heat the pool water. Imagine how difficult that would be if a gas pipe fitting can't be anywhere near it.
 
The gas is supposed to be inside the tank and the piping, how is a spark on the outside going to ignite it?

Arts 500-516 does not even consider this a classified location,as long as there is no kind of activity going on where that gas is ordinarily released into the area in question.

If there were a cylinder refilling station there, then you have a different situation.

Occasional refilling of a fixed tank via a transfer truck, I don't even think triggers a hazardous location. There is only a limited time potential for release of gas, and it will then be a long time before it may happen again.


Any automatic pressure relief valves may be required to pipe the release to a safe area though.
 
NFPA-58 has a 10' foot rule from what I could find

NFPA-58 has a 10' foot rule from what I could find

The gas is supposed to be inside the tank and the piping, how is a spark on the outside going to ignite it?

Arts 500-516 does not even consider this a classified location,as long as there is no kind of activity going on where that gas is ordinarily released into the area in question.

If there were a cylinder refilling station there, then you have a different situation.

Occasional refilling of a fixed tank via a transfer truck, I don't even think triggers a hazardous location. There is only a limited time potential for release of gas, and it will then be a long time before it may happen again.


Any automatic pressure relief valves may be required to pipe the release to a safe area though.

I was searching around the internet and found NFPA-58 has a 10' rule from the relief valve or filling connection to a source of spark. We ended up moving it closer to the new location of the pool equipment. I believe just a like a gas inta-hot water heater with a disconnect or cord and plug I believe it would have been fine and not a source of spark.

Thanks for your input.
 
I was searching around the internet and found NFPA-58 has a 10' rule from the relief valve or filling connection to a source of spark. We ended up moving it closer to the new location of the pool equipment. I believe just a like a gas inta-hot water heater with a disconnect or cord and plug I believe it would have been fine and not a source of spark.

Thanks for your input.
Yes, relief valve outlet or a filling connection can trigger a hazardous location, those would't necessarily have to be in same vicinity as the tank.
 