Articles 210 and 215 contain an exception that conductors and overcurrent protection can be sized for the sum of the continuous (not 125%) plus non-continuous load if the entire assembly is listed for operation at 100 percent of its rating.
Does the 100 percent assembly rating have anything to do with 90 degree C equipment and/or conductor temperature provisions? For example, can a 100 percent rated assembly only be used with 90 degree C rated enclosures, terminations, and conductors?
Does the 100 percent assembly rating have anything to do with 90 degree C equipment and/or conductor temperature provisions? For example, can a 100 percent rated assembly only be used with 90 degree C rated enclosures, terminations, and conductors?