or something to that effect. That way I wont be told I have an 80% rated cb when an 80% rated cb does not exist.
The regular cb is rated for 100%. You just have to multiply your continuous loads by 125% and then add 100% of the non-continuous, and as long as that value is less than the marked rating of the cb, you can put it on there. Yes you can load a 100A cb to 99A, you can even go to 100A. but 100.1A is not allowed.
"This one does not go to eleven." http://youtu.be/N3L4EZwmRrA?t=3m34s
The regular cb is rated for 100%. You just have to multiply your continuous loads by 125% and then add 100% of the non-continuous, and as long as that value is less than the marked rating of the cb, you can put it on there. Yes you can load a 100A cb to 99A, you can even go to 100A. but 100.1A is not allowed.