Sparky2791
Senior Member
- Location
- Northeast, PA
- Occupation
- Electrical Design
I did service calculations for a school based on 220.86 and the service load after calculation comes to 580A. This is a complete renovation of the school including upgrading the existing main distribution panel with a new service disconnect (Main Circuit breaker) According to the calculations the 600A service is adequate, obviously sized very close but the school is served by a campus distribution and upgrading the transfomer to bring in a larger service is not only cost prohibitive but the lead time for a transfomer in this current market is unreal. I recommended that a service upgrade be considered moving forward but the 600A is adequate to serve their immediate needs. My question is if the main service disconnect must be a 100% rated circuit breaker? Connected load is 711A so realistically the building will only see 60% of that as a peak demand an that is being generous.
The building does have a full 600A of conductors feeding it .
Thanks for your replies.
The building does have a full 600A of conductors feeding it .
Thanks for your replies.