It depends on whether the standard rated breaker would cause you to go to the next size after doing your load calculation and if the 100% rated breaker was available in the equipment and was worth the extra cost.
https://iaeimagazine.org/magazine/2016/07/19/100-vs-80-choosing-the-right-ocpd-solution/
Yes you can use a smaller conductor because you can use 100% of load instead of 125% of load. Also this 125% only applies to continuous load (for standard breakers) when selecting conductor ampacity needed.So basically, the 100% breaker allows us to not derate the conductors for continuous loads and thus saves on conductor costs?
Is it just me or would anyone else get nervous running a breaker at 100% ? I have had breakers trip at 80% in some high ambient temp situations.
Yes you can use a smaller conductor because you can use 100% of load instead of 125% of load. Also this 125% only applies to continuous load (for standard breakers) when selecting conductor ampacity needed.
I was always told a major reason they require 125% for standard device is because the device sinks some of the heat it produces into the conductor - and it is for the termination temp rating more then anything. 100% breakers supposedly don't depend on conductor as a heat sink is one of their major differences over a standard device.
It depends on whether the standard rated breaker would cause you to go to the next size after doing your load calculation and if the 100% rated breaker was available in the equipment and was worth the extra cost.
https://iaeimagazine.org/magazine/2016/07/19/100-vs-80-choosing-the-right-ocpd-solution/
Isn't there also something about 90*C terminations on the breaker?
IIRC, you are still restricted to 75 degree terminations. 100% breakers, again IIRC, require 90 degree rated conductors used at 75 degrees (mostly an academic requirement these days).
I was always told a major reason they require 125% for standard device is because the device sinks some of the heat it produces into the conductor - and it is for the termination temp rating more then anything. 100% breakers supposedly don't depend on conductor as a heat sink is one of their major differences over a standard device.
That is correct on 125%. By requiring the breaker to be rated at 125%, or limiting the load to 80%, in effect you are increasing the size of the conductor, which creates a heat sink.
Never installed one but seem to recall reading you typically must use 90C conductor selected from 75C ampacity table.Isn't there also something about 90*C terminations on the breaker?
Yes, sort of. The issue is that you cannot buy a "100% rated" breaker as a component and install it yourself in the field. Unless you ARE the switchgear OEM, the ONLY way you can buy a 100% rated breaker is in an ENCLOSED piece of gear where the ENTIRE ASSEMBLY is tested and listed for 100% current. So a Main CB on a switchboard is a perfect example; you don't order a switchboard, then order a 100% rated breaker to put inside of it, you order a switchboard WITH a 100% rated main breaker; they have to be listed together. In addition, you will never find a FEEDER breaker in a switchboard or panelboard that is 100% rated. You have to move up to switchGEAR where each breaker is inside of its own cubicle to get that....
In terms of the breakers, I remember someone saying they are exactly like regular breaker, just with provisions for air flow, cooling and spacing.
Yes, sort of. The issue is that you cannot buy a "100% rated" breaker as a component and install it yourself in the field. Unless you ARE the switchgear OEM, the ONLY way you can buy a 100% rated breaker is in an ENCLOSED piece of gear where the ENTIRE ASSEMBLY is tested and listed for 100% current. So a Main CB on a switchboard is a perfect example; you don't order a switchboard, then order a 100% rated breaker to put inside of it, you order a switchboard WITH a 100% rated main breaker; they have to be listed together. In addition, you will never find a FEEDER breaker in a switchboard or panelboard that is 100% rated. You have to move up to switchGEAR where each breaker is inside of its own cubicle to get that.
In that 100% listing, the breaker testing procedure may have (usually have been) listed using 90C rated conductors, but you cannot use the conductors at their 90C ratings, you must still use them at their 75C ratings. So it changes nothing with regard to the conductors if you are already using 90C insulation.
At 1600A? Probably significant compared to a 2000A breaker used at 80%, because for some mfrs that's a frame size and classification change. But it really depends on that issue. So for example if a mfr doesn't offer a 1600A frame MCCB and would give you a 2000AF ICCB with a 1600A rating plug, then there is no difference in price.Any idea of the extra cost an 100% breaker scheme?
Yes, sort of. The issue is that you cannot buy a "100% rated" breaker as a component and install it yourself in the field. Unless you ARE the switchgear OEM, the ONLY way you can buy a 100% rated breaker is in an ENCLOSED piece of gear where the ENTIRE ASSEMBLY is tested and listed for 100% current. So a Main CB on a switchboard is a perfect example; you don't order a switchboard, then order a 100% rated breaker to put inside of it, you order a switchboard WITH a 100% rated main breaker; they have to be listed together. In addition, you will never find a FEEDER breaker in a switchboard or panelboard that is 100% rated. You have to move up to switchGEAR where each breaker is inside of its own cubicle to get that.
In that 100% listing, the breaker testing procedure may have (usually have been) listed using 90C rated conductors, but you cannot use the conductors at their 90C ratings, you must still use them at their 75C ratings. So it changes nothing with regard to the conductors if you are already using 90C insulation.
At 1600A? Probably significant compared to a 2000A breaker used at 80%, because for some mfrs that's a frame size and classification change. But it really depends on that issue. So for example if a mfr doesn't offer a 1600A frame MCCB and would give you a 2000AF ICCB with a 1600A rating plug, then there is no difference in price.
But that said, 1600A is the upper typical limit of "Molded Case Circuit Breakers" (MCCBs) listed under UL489. There are also UL 489 listed "Insulated Case Circuit Breakers" (ICCB) from some mfrs, but they have pretty much gone by the wayside as a separate design in that most mfrs now just sell you a "lighter duty" Power Breaker with a UL 489 listing, instead of a UL 1066 listed Power Circuit Breaker (PCB). PCBs and ICCBs are almost always going to be 100% rated, but they are typically a lot more expensive than MCCBs.
Never installed one but seem to recall reading you typically must use 90C conductor selected from 75C ampacity table.
There is a simple chart on page 2 of this pdf fileOk- here comes the dumb question, but what is the difference between modeled case, insulated case and power circuit breakers? What are minimum and max for each?