I have a landlord switchboard that feeds a tenant meter bank with a 4 wire + ground feeder, if the tenant connected load is equal to 192A Connected and 140A demand (kitchen equip, hvac, general purpose lighting and receptacles) the max the meter / main can accept is a 200A c.b. in leau of providing a new feeder from the utility or switchboard and providing a new meter / ct with a new meter does anyone know if these can have 100% rated c.b. to feed the tenant space? I could not find in the manufacturers literature where it says it cannot? the current service is a #300kcmil (al) + grd to a wireway that feeds two panels one with a 225A main and the other with a 200A main fed from the tapped feeder to the panel. the 200A mcb panel (existing tenant panel) only has 6 circuits for general purpose lights and receptacles all the equipment is fed from the adjacent panel