ryangittens
Member
- Location
- usa
Ref. NEC 2020
Per 705.12(B)(3)(3) as I understand it the feed through panel needs to be counted. If the feedthrough has a 200A main that would make adding any size breaker to meter-main panel non-compliant. However if you place the solar/source breaker at the end of the meter main I don't see any way of overloading the bus bars and everything seems properly protected. There is no code section for this but wanted to see what your thoughts were.
Under 2020 this may not fly but 2023 705.12(B)(6) allows for engineering calculations.
Per 705.12(B)(3)(3) as I understand it the feed through panel needs to be counted. If the feedthrough has a 200A main that would make adding any size breaker to meter-main panel non-compliant. However if you place the solar/source breaker at the end of the meter main I don't see any way of overloading the bus bars and everything seems properly protected. There is no code section for this but wanted to see what your thoughts were.
Under 2020 this may not fly but 2023 705.12(B)(6) allows for engineering calculations.