There is a thread somewhere in the post, that explains th rational. In higher voltage distribution systems an sustained arcing ground his an impedance that is below the thresholds of OCP's, the sustained arcing ground faluts can burn to the point where the ground fault current exceeds the OCP rating and opens the device or becomes a phase to phase faultgenerating sufficent current to operate the OCP device.
I located the thread.
http://forums.mikeholt.com/showthread.php?t=83034&highlight=ground+fault
From that thread
Overcurrents and Undercurrents All About GFCIs?.
Author Earl W. Roberts,
1996, Mystic Publications
This book also covers GFPE, from chapter 12 (my abridged version)
While arcing faults can occur on 120/208 VAC systems the arc does not result in a restrike arc due to the voltage level. Studies have shown that to have a restriking arcing ground fault the voltage levels of 374 volts are necessary.
120X1.414 = 169.68, Peak Voltage
277X1.414 = 391.67. Peak Voltage
GFPE is required on 277/480 VAC distribution systems to protect against the devastating damage that occurs from these sustained restriking arcing ground faults, it is not required on 120/208 distribution systems as the restriking high impedance burn down arcing ground faults are not occurring.