JJcrick2
Member
- Location
- Columbus, OH
- Occupation
- Telecommunications Engineer
Hello. I'm a telecommunications engineer for a public utility in Ohio.
We are creating a wiring standard for remotely connecting and monitoring our LP tank fuel levels at our remote telecom sites. The tanks provide fuel for backup generators that are located in our industrialized buildings at the site.
Summarization of the monitoring circuit:
The LP tanks have a Rochester gauge with a hull effect sensor that translates the fuel level to an electrical signal (4.5-5.0 vdc @4.5mA). The electrical signal is carried on a conductor that is ran in a 1” underground conduit to our telecom building. In the buildings, the electrical signal passes through a surge arrestor before it passes through to an analog card in an rtu. The rtu is polled over an internal network and the fuel level is remotely monitored by our NOC Team that monitors our entire AEP internal infrastructure.
We are trying to determine the National Electric Code hazardous location classification of the LP tanks we use at our remote telecom sites. The tanks are located outside, over 10’ away from our un-manned telecom buildings and only are used for the fuel supply of our backup generators. Do you know if the tanks are considered Class I, Division 1 or Class I, Division 2?
Rochester, the manufacturer the fuel gauge indicated this is a Class 1 Division1 environment. However, after talking with the State of Ohio, it seems this is open to NEC interpretation and could be classified and Class 1 Division 2.
Thanks for your assistance,
Jeff
We are creating a wiring standard for remotely connecting and monitoring our LP tank fuel levels at our remote telecom sites. The tanks provide fuel for backup generators that are located in our industrialized buildings at the site.
Summarization of the monitoring circuit:
The LP tanks have a Rochester gauge with a hull effect sensor that translates the fuel level to an electrical signal (4.5-5.0 vdc @4.5mA). The electrical signal is carried on a conductor that is ran in a 1” underground conduit to our telecom building. In the buildings, the electrical signal passes through a surge arrestor before it passes through to an analog card in an rtu. The rtu is polled over an internal network and the fuel level is remotely monitored by our NOC Team that monitors our entire AEP internal infrastructure.
We are trying to determine the National Electric Code hazardous location classification of the LP tanks we use at our remote telecom sites. The tanks are located outside, over 10’ away from our un-manned telecom buildings and only are used for the fuel supply of our backup generators. Do you know if the tanks are considered Class I, Division 1 or Class I, Division 2?
Rochester, the manufacturer the fuel gauge indicated this is a Class 1 Division1 environment. However, after talking with the State of Ohio, it seems this is open to NEC interpretation and could be classified and Class 1 Division 2.
Thanks for your assistance,
Jeff