Okay, you have (or will rent) 480/277.
Do you need the neutral on the 600V side?
An autotransformer (buck/boost) arrangement is probably the way to go, you can get your 1000kVA capacity with 200kVA worth of transformer.
If you don't need the neutral, then 2x 100kVA 480:120V transformers in an open delta boost configuration would do the trick.
If you do need the neutral then you would need 3x 67kVA 277:69V transformers in a wye configuration. That isn't a common transformer rating, but it is the same ratio as 480:120V. You could use 3x 100kVA 480:120V single phase transformers and be a bit scant on the rating (a 100kVA 480V transformer used at 277V works just fine but can only handle 58kVA).
Note that a 480-120 transformer is most commonly available with dual voltage primary and secondary, eg 240/480 - 120/240.
Jon