not sure what size the generator is in this scenario that has been partially described to me, so I'm going to use hypothetical to explain my confusion.
Let's say you've got a 1000A ATS associated with a 1000A feeder to a 3 phase, 3 wire DP with only 3 phase motors on it.
The 1000A part tells me that I'm going to have to have ground fault protection. Where there is ground fault, I would normally provide a 4 pole transfer switch and bond the neutral to ground at the generator. i.e. as a SDS.
So in this scenario where there is no need for a neutral, there is therefore no need for 4 pole transfer switches and at the generator there will be no neutral to bond to ground. So, is the generator in this case a SDS? Is there anything wrong with the system I describe above?
Thanks,
Mike