dm9289
Industrial Maintenance Electrician
- Location
- Pennsylvania
- Occupation
- Industrial process repair/ maintenance Electrician
We are replacing some breakers and contactors for a heating grid and I was not sure our cable had the proper ampacity.
Basically we have a heating grid 220v that draws 600 amps on or off no throttling
My thoughts were this would be treated as a continuos load NEC 210.19A and 427.4
So I feel we need cable or cables rated at 600A x 1.25= 750A
Can anyone help me on the ratings of asbestos ava cable 1000kcm
Basically we have a heating grid 220v that draws 600 amps on or off no throttling
My thoughts were this would be treated as a continuos load NEC 210.19A and 427.4
So I feel we need cable or cables rated at 600A x 1.25= 750A
Can anyone help me on the ratings of asbestos ava cable 1000kcm