Hello, I'm having some issues with an Acme Electric transformer. It seemed to be bad in an existing piece of HVAC equipment, after replacement it still had the same issue on the secondary. The feed is good, seemingly. The power for the transformer is a 2 pole 480 volt from a 3 phase 480 volt delta circuit for the unit and the secondary should be a 2 pole 240 volt. However, upon measuring the secondary it reads 150 volt leg to ground and 85 volt leg to ground. Phase to phase is 240. Is this a grounding/neutral issue? There is no center point terminal for neutral on the secondary. From the initial contractor install, years ago, it has worked fine. Could it be something back feeding from down stream? There have been some recent installments of power analyzers and conditioning equipment in the building, which coincidentally, were done right before this interruption occurred. That may be of no concern though. Thanks for any help on this.