1000W HPS light ballast and remote receptacle

Status
Not open for further replies.

sammynewberg

New member
Is it ok to mout a ballast in one room that plugs into a special receptacle, and run the cord from the ballast to the 1000W lights through the wall? I am asked to bid on a medical marijuana growing facility (there are a lot of them now in Denver) and the engineered drawings show about 20 ballasts that are to be mounted in a hall on either side of the hallway. Each ballast pulgs into a special receptacle. Then the growing lights are to be installed in 'grow' rooms on either sides of the hall, where the lights will 'plug' into these ballast (which seems to me to be more of a controller).
Is this even code compliant?
 

jumper

Senior Member
Is it ok to mout a ballast in one room that plugs into a special receptacle, and run the cord from the ballast to the 1000W lights through the wall? I am asked to bid on a medical marijuana growing facility (there are a lot of them now in Denver) and the engineered drawings show about 20 ballasts that are to be mounted in a hall on either side of the hallway. Each ballast pulgs into a special receptacle. Then the growing lights are to be installed in 'grow' rooms on either sides of the hall, where the lights will 'plug' into these ballast (which seems to me to be more of a controller).
Is this even code compliant?

Probably not:

400.8 Uses Not Permitted. Unless specifically permitted
in 400.7, flexible cords and cables shall not be used for the
following:
(1) As a substitute for the fixed wiring of a structure
(2) Where run through holes in walls, structural ceilings,
suspended ceilings, dropped ceilings, or floors

(3) Where run through doorways, windows, or similar
openings
(4) Where attached to building surfaces
Exception to (4): Flexible cord and cable shall be permitted
to be attached to building surfaces in accordance with the
provisions of 368.56(B)
(5) Where concealed by walls, floors, or ceilings or located
above suspended or dropped ceilings
(6) Where installed in raceways, except as otherwise permitted
in this Code
(7) Where subject to physical damage
400.9 Splices. Flexible cord shall be used only in continuous
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Sammy:

1. Welcome to the forum. :)

2. If the ballasts and lamp-holders are in suitable enclosures, you should be able to run appropriately-insulated conductors through a properly-terminated conduit or flexible raceway. (Lotta qualifiers. ;))

3. Can I come work with you? :grin:
 
I think your best bet is to check with the AHJ and verify if they will allow such an install.... I assume your in California as there are not too many other areas that allow Medical use. Rules vary greatly from local to local in this State.

seems to me 1000 watters could just as easily (and cost efficiently) be hard wired with a toggle switch instead of a cord & plug method. Depending on how many of them turn on and off at certain times, a timer & lighting contactor might be the most efficient solution to reduce human error for the industrial environment.
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
This has been legal in Oregon, Washington and California for a wile now, and since we get so much rain here and have the low cost electricity farmers use these systems in green houses for all types of starts anyways. We have seen this allot. I wired a show room for a indoor agricultural lighting store. I used 2 200A panels and 1 150A, all 20A branch circuits and 40A rated contactors. Ballast units mount on unistrut above the hood.
Remote ballasts is a more and more common question I get. From pastry cases to ag lighting.
Article 410.30(C)(1) Condition (1) requires The luminaire (fixture) is located directly below the outlet or busway. That includes the ballast.

Here is 410.30(C)(1);
" Electric-Discharge Luminaires (Fixtures)
(1) Cord-Connected Installation A listed luminaire (fix-
ture) or a listed assembly shall be permitted to be cord
connected if the following conditions apply:
(1) The luminaire (fixture) is located directly below the
outlet or busway.
(2) The flexible cord meets all the following:
a. Is visible for its entire length outside the luminaire
(fixture)
b. Is not subject to strain or physical damage
c. Is terminated in a grounding-type attachment plug
cap or busway plug, or is a part of a listed assembly
incorporating a manufactured wiring system connec-
tor in accordance with 604.6(C), or has a luminaire
(fixture) assembly with a strain relief and canopy"

1000W or HPS / MH remote ballasts are really a 2 capacitors and a constant wattage autotransformer in an aluminum housing?

Could you request/propose an alternate installation method to the manufacturer allowing a 1/2" KO to be drilled in to the housing and flex in to the unit, remove the inlets and blank off the holes with panel blanks, or use RE washers and pipe into one of the rectangular panel inlet mounts?

You might have it drawn up and submit it to the manufacturer or find a listed product that provides a 1/2" K/o. I think I remember some custom baseball pole lights that had a ballast in a generic 3R box 1/2way up the pole that did 2 heads. I don't reacll if it was a listed product or UR components. Ask your inspector what he/she will require.

NOTE: There is a maximum distance that ballast can be from the screw shell.

With the agricultural hoods and remote ballasts however you will need the proprietary hood connector to mount on a four square raised cover? Can the manufacturer supply that as a listed product? I don't think you want to use a regular twistlock up there. Or you can hard wire the hood also.

The thing that always concerns me about any HID lighting is when the people designing and selling this stuff recommend using 30A or 50A branch circuits.
I remember working as an apprentice 15 years ago on highbay 400W MH lighting and installing 15A twistlocks on a 277V 30A branch circuit. I did not like it.
I still see this once in a wile on pole lights or parking lot lights.

210.21(B)(3) Exception 2 sends you to 410.30(C) Which paragraph (2) allows a 6-15 15A 240V receptacle to be on a 50A branch circuit as long as you meet 240.5. (1)
I seen these green house or hot house agricultural lighting installations have 30 and 50 amp branch circuits wired in to a typical intermatic timer and 6-15 receptacles taped off the load side on 12AWG wire.
I am of the opinion that the maximum size circuit can be 20A or in the case of a 240V branch circuit 3 1000W lamps.
20A branch circuits require a few contactors or latching lighting relays. For a large system like you are doing you should look into GE latching type lighting controls and a sequencer that pluses each 20A latching relay circuit a second or two apart. Then you don't have the inrush.
410.30(C)(2):
"(2) Provided with Mogul-Base, Screw-Shell Lampholders
Electric-discharge luminaires (lighting fixtures) provided
with mogul-base, screw-shell lampholders shall be permitted
to be connected to branch circuits of 50 amperes or less by
cords complying with 240.5. Receptacles and attachment
plugs shall be permitted to be of a lower ampere rating
than the branch circuit but not less than 125 percent of the
luminaire (fixture) full-load current."
240.5(1) basically states you have to go with manufacturer recommendations.
"240.5 (1) Supply Cord of Listed Appliance or Portable Lamps
Where flexible cord or tinsel cord is approved for and used
with a specific listed appliance or portable lamp, it shall be
considered to be protected when applied within the appliance
or portable lamp listing requirements."
So the manufacturer should state the max size branch circuit the remote cord and plug ballast/hood unit can be on (if more than 20A).

One other thing to remember is I think 410.48 requires a 2 pole contactor if you are using both hots of a 240V system. I was just asked about this by maintenance person whom got shocked by the screw shell relamping a 240V HID lamp. People think it is OK because you could turn off the breaker when relamping.

Hope that helps
 

wankster

Member
most of the agricultural ballasts come with propriety hard wired pigtails on the secondary side. removing/cutting the pigtail voids warranty.
 

wankster

Member
But you still cannot run the cord through the wall. :)

right.;) what i'm getting at is they do not lend themselves to hard wiring. they seem to have a plug-and-play theme that undoubtedly is much appreciated by their target demographic:grin:

IMO, if you had to run them in a separate room (if its even legal to have the ballast that far away) your best bet would be to get some of the lamp to ballast cords and cut the lamp end off and hard wire it to a j-box on one end and plug it in to the ballast on the other. Then you could run the conductors in through conduit, thus eliminating your cord through wall dilemma. of course, then you would have to butcher another propriety cord on the lamp side to hard wire to your secondary lines. i believe that side is doable without voiding any warranties. on thing is for certain, you will need lots of propriety cords! The best part is, you cant buy the propriety ends to make your own cords.
 
Last edited: