My son lives in a remote area of Africa. His power (240v 50cycle) is only available at limited times so he uses solar power a lot. I'm trying to help him figure out how to run a U.S. flux core wire feed welder (120V 60cycle) off a 1000W inverter. Obviously a welder with a 20 amp input rating running at full bore won't work but if it's set at a low enough output wouldn't that work? I've seen nameplates showing 25amps at 15.2V DC output.
I highly suspect you have already thought of everything I got. My suggestions are right up there with, "Check to see if the computer is turned on"
Assuming the welder is already purchased.
Is the existing 1000W inverter 240, 50HZ output? I suspect it is.
I don't know how picky the welder is about the input power frequenct/waveform. Consider calling the welder mfg as ask them about power input specs
As already mentioned, transform down to 120V, 50 hz, as see if it will run.
Purchase a secondary inverter just for the welder. Can you send him an inverter with a 120V, 60hz output - get a 2kw inverter.
I've had three different small wire feed welders over the last 20 years. All three were convertable - either 120V or 240V input. I suspect you already know this one is not.
good luck. Let us know how it comes out.