So I know this has been hashed on for a while, but looking back through the history I can't seem to get a good answer. I'm adding a subpanel in my garage to power a current plug-in car and perhaps a future one, as well as maybe an outlet for a future welder. 100A subpanel even though I'll only be populating one 40A circuit for the current charger. Cable run is about 120feet.
I'm thinking Aluminum SE cable though the walls because, well, I'm cheap. Running over the roof (flat roof) with EMT is also a possibility, but Cu THWN is still a lot more costly than than Al SE. Plus, I'm in Arizona and I think I'd have to use a 0.58 correction factor if I went over the roof, so my Cu may actually end up being bigger than an Al cable run through the walls. For these reasons I'm leaning toward the SE cable and a bunch of drywall patches.
Problem is, for the life of me can't nail down what size SE cable I need. #2, #1 or #1/0?? I called the local building department and they told me they just always use the 90 degree column of 310.15(B)17 (yep, that's the one they pointed me to). So they'll accept a #4 all the way up to 115A, but I KNOW that they're misreading the code (or at least they're not fully understanding the other sections).
So 310.15(B)(6) indicates #2, but I'm pretty sure I can't use this because it's a subpanel and doesn't supply "all loads that are part of the dwelling unit". So my best guess is the 310.15(B)16 75 degree column which points me to #1. However, in the 100' run, there is a 3' section that runs through some insulation, so maybe I need to step all the way down to the 60 degree column, and then I'll need a #1/0.
Ultimately I just want it to be safe, and I'm going to be drawing a lot of energy through this daily (at least 20kWh daily with one car. Significantly more if we get a second fully electric), so I don't want a lot of transmission loss. If you guys point me to #1/0 I'll do that, but it's going to kill me pulling that donkey dong through the walls. I'm hoping #1 will suffice.
I'm thinking Aluminum SE cable though the walls because, well, I'm cheap. Running over the roof (flat roof) with EMT is also a possibility, but Cu THWN is still a lot more costly than than Al SE. Plus, I'm in Arizona and I think I'd have to use a 0.58 correction factor if I went over the roof, so my Cu may actually end up being bigger than an Al cable run through the walls. For these reasons I'm leaning toward the SE cable and a bunch of drywall patches.
Problem is, for the life of me can't nail down what size SE cable I need. #2, #1 or #1/0?? I called the local building department and they told me they just always use the 90 degree column of 310.15(B)17 (yep, that's the one they pointed me to). So they'll accept a #4 all the way up to 115A, but I KNOW that they're misreading the code (or at least they're not fully understanding the other sections).
So 310.15(B)(6) indicates #2, but I'm pretty sure I can't use this because it's a subpanel and doesn't supply "all loads that are part of the dwelling unit". So my best guess is the 310.15(B)16 75 degree column which points me to #1. However, in the 100' run, there is a 3' section that runs through some insulation, so maybe I need to step all the way down to the 60 degree column, and then I'll need a #1/0.
Ultimately I just want it to be safe, and I'm going to be drawing a lot of energy through this daily (at least 20kWh daily with one car. Significantly more if we get a second fully electric), so I don't want a lot of transmission loss. If you guys point me to #1/0 I'll do that, but it's going to kill me pulling that donkey dong through the walls. I'm hoping #1 will suffice.