You can use #2 Al to feed a 100A subpanel if it's on a 100A residential service. But you can't do so on a larger residential service, because you only are allowed the 83% factor for a collection of loads with the full diversity of a dwelling unit.I don’t understand why we can’t use #2 AL to feed a 100A subpanel but we can use it to run a 100A service.
If the service size is above 100A, no, it won't be OK. Find larger conductors or a smaller breaker.Can’t find 1 nor 1/0 quadruplex around me nor can I find a 90A breaker! Will 100 be ok?