104/208 volt single phase motor

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Most single phase dual voltage motors are simply made with two Main windings that are put in series for the higher voltage and parallel for the lower. When the dual voltage is 120/240V, that is simple and useful. But if someone wanted a motor TRUELY designed to operate at 208V, then indirectly, the lower voltage will end up as 104V. The lower voltage rating is not useful for anything though (outside of parts of Japan maybe...)

What MOST motor mfrs do however is to just design the windings such that the 230V setup is OK down to 208V.
 

Birken Vogt

Senior Member
Location
Grass Valley, Ca
The same ratio of 230/240 would put 220 util. at 211 so it does not exactly line up. I have seen a lot of motors from that era that were stamped 110/220/440 volts on the nameplate but never anything else.
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
Anyone ever seen such a thing? I've got one here, just never seen that on a data plate of a motor before. There is no question other than that, I won't be using this motor, probably just yard art.

There are some of these out there that are still used today. On 120V.
I’m inclined to agree with Larry in post 11.
 

Jpflex

Electrician big leagues
Location
Victorville
Occupation
Electrician commercial and residential
Anyone ever seen such a thing? I've got one here, just never seen that on a data plate of a motor before. There is no question other than that, I won't be using this motor, probably just yard art.
Nope and where you find such a transformer power source for 104 volts perhaps changing taps stepping down from 120 to near 104 volt secondary although not good for the transformer? Of course running the motor at common 208 volts would be the best option
 