Why the Elec. Technicaian using '100amps' contact resistance tester instead of '10Amps' tester to test 3000Amps bus bar connections?

Can anybody give an explanation for this?
 

zog

Senior Member
Location
Charlotte, NC
It is a matter of accuracy, the higher the test current the more accurate the readings will be at lower readings. A 3000A bus connection will have a very low reading so accuracy is important.
 