Question, and my apologies if this is a motors 101 question please take it easy I am not a calc guy.
A 10 HP motor 208/3ph is being replaced, one of the conduit runs feeding it is stuffed with 9 CC so presumably the existing #8 cu needs a 70% derate 55 X .7 = 38.5A
Now the wire has to have an ampacity of 125% of the value in table 430.250.
I go to the table and a 208V 10HP motor is 30.8 A
30.8 X 1.25 = 38.5
But in the 200V column its 32.2A
32.2 X 1.25 = 40.25
So which column is correct?
There is not a 440V and a 480V column so why 200 and 208?
Thank you.
30.8 X 1.25 = 38.5
32.2 X 1.25 = 40.25
Thank you.