hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
I 10kva 208V three phase inverter/battery supplying 60A MLO panel A. The inverter/battery is for loads NEC 2017 Section 700.12(A)
Demand load on Panel A is 3kva.
panel B has 60 A feeder breaker supplying the inverter/battery.
So what it looks like is shown attachment.
1. Would not the 60A breaker be too large for 10kva 208V three phase inverter/battery?
2. If power goes out then in inverter/batter is feeding the MLO panel board 60A. Their is no breaker upstream that is protecting the Panel A. Should not battery/inverter have output breaker?
Demand load on Panel A is 3kva.
panel B has 60 A feeder breaker supplying the inverter/battery.
So what it looks like is shown attachment.
1. Would not the 60A breaker be too large for 10kva 208V three phase inverter/battery?
2. If power goes out then in inverter/batter is feeding the MLO panel board 60A. Their is no breaker upstream that is protecting the Panel A. Should not battery/inverter have output breaker?