Here goes......
Proposing the installation of a 10 kW electric unit heater in a residential attached garage. Calculated load for the heater is 41.667 Amp. Wiring to be #6 THHN /THWN in 3/4 emt.
Based upon article 424.... 60 Amp breaker? Right... Heater could run for more than 3 hours, and chances of finding a "residential plug in breaker rated for 100% duty are slim.
Stop me when I'm wrong
Howard
Proposing the installation of a 10 kW electric unit heater in a residential attached garage. Calculated load for the heater is 41.667 Amp. Wiring to be #6 THHN /THWN in 3/4 emt.
Based upon article 424.... 60 Amp breaker? Right... Heater could run for more than 3 hours, and chances of finding a "residential plug in breaker rated for 100% duty are slim.
Stop me when I'm wrong
Howard