Quick question:
Changing out a new heat pump from 9.8KW to 10KW...data plate says 9.6 KW on the heater coil...do i do the math with 10 or 9.6 to size the wire?
10000/240=41.666x125%=52.08 amps=#6awg@75degreeTHHW
9600/240=40x125%=50amps=#8awg@75degreeTHHW
Am I a knucklehead and should start doing plumbing instead of electrical? :smile:
Changing out a new heat pump from 9.8KW to 10KW...data plate says 9.6 KW on the heater coil...do i do the math with 10 or 9.6 to size the wire?
10000/240=41.666x125%=52.08 amps=#6awg@75degreeTHHW
9600/240=40x125%=50amps=#8awg@75degreeTHHW
Am I a knucklehead and should start doing plumbing instead of electrical? :smile: