I am dealing with a local plan reviewer that has denied me a permit on an air conditioner change-out that has a 6ga Romex type wire.
He states that nm wire must use the 60c scale which puts max. amps at 55.
The a/c manufacturer rates 10kw heater/air handler at 58.6a mca and 60a mop.
It also rates an 8kw heater @ 50.3 mca and 60a mop.
Using these two examples it would require a 4/0 wire for either heater.
I have tried to have him allow the 8% increase and he stated that NFPA 70 does not allow exceptions to the 60c scale.
Any thoughts?