Checking out a friend's house with flickering lights. This only happens under load. Fridge, dryer, ac, etc.
Get to his house, main breaker panel with back to back meter. Check panel and service conductors in panel are fine.
Go outside and find that ground wire is disconnected from ground rod. Same with the neighbor 20 feet away.
Neighbors house has 12v ground rod to hose spigot, my friends house has 5v gnd rod to spigot.
These readings are with gec disconnected, so measuring straight to earth.
Did the neighbor lose a neutral? transformer lose a neutral?
Both homes are fed from the same transformer.
Sent from my SM-G965U using Tapatalk