110.14(A), rule for conductors on a terminal
Alabama
Home Builder Unlimited
Hey Mike Holt Enterprises, should 110.14(A) read …one conductor ‘end’ or terminal, instead of one conductor or terminal? When someone strips at mid-wire, and wraps a screw, and has what looks like two wires coming out from the screw and no ends, is this permitted by 110.14? In my mind I’m struggling with the power source coming TO this screw may be one conductor, and even though the wire isn’t cut, would the part coming FROM the screw be considered a second conductor, as it’s purpose is feeding out, once it leaves the screw connection?
This is done everyday, especially in multigang switch boxes. It cuts down on box crowding from wire connectors for splices.
As for the conductor being counted as two conductors, it wouldn't add to box fill as the conductor doesn't leave the box in the above scenario.
Also, for it being two conductors if it feeds something outside the box, it wouldn't be any more conductors than a spliced cable leaving the box.
I see nothing in 110.14(A) preventing this if the conductor has a good connection and isn't damaged from stripping the insulation. Stranded wire could be a problem if some of the strands are cut when stripping.
Other than that, I see no problem.
Wrapping a screw is a work man ship issue. It is one of the don'ts in the handbook version of NEC or if you have link, just use the expanded content. No different than going the wrong direction. That being said, it is the least of concern for issues involving screws & conductors, in my opinion. Especially if we are talking EGCs. You just can't make good contact if it wraps. I am sure there is some NEMA or UL issue or something.
They should be using pressure connector terminals and not a screw if they want to do that. Below photo as an example.
1761064248468.png vs
There is no reason not to loop the conductor around the screw of a wiring device. The picture in post 3 just shows poor workmanship when the conductor was looped. I worked on two different jobs where the project specifications required that the conductor be looped around the receptacle screws for specific circuits.
How is a wrapped conductor any different than a fork terminal? Both of the have one portion being pulled under the binding screw while the other side is being pushed out. Many binding screws are designed and listed to make contact with a straight conductor.
There is no doubt your picture is a poor connection because the conductors are laid over themselves rather than being flat not because they are looped, regardless what the handbook authors opinion is.
  • Like
Reactions: J2H
The first time I saw a contractor do this on every receptacle he pointed out that on his circuits were basically one continuous run with no "connections". Fewer connections = fewer loose connections.
He was skilled at it...looping his Romex at each box and stripping not cutting.
I’ve seen it spec’d in components listed as part of the assembly’s wiring that showed on the schematic as factory, and others showed as field wiring, I believe it was conveyor controllers and some of their ICPs were like that and some weren’t, that was back in the 80’s at WMC/WC, and they might have been export products, I can’t remember. I just remember seeing the loop mid-span stripping being done both in the factory facilities and out in the field, as I also moonlighted as an installer besides the plant floor and some R&D. I do remember the conductor ampacities were being pushed to about their maximum, like within an amp, and the engineers were very focused on how the loop was made, like how a surgeon would do it, because they experimented with repeatedly bending and unbending, and you know how that turned out, so we were provided very explicit instructions for the loop stripping, bending properly (flat and perfect radius the first time), and terminating while holding it pinched (but not overly tightly) while tightening the screw. I wasn’t in the code books as a worker, but later in life could never find it permitted or prohibited, and noticed an absence of it in any receptacle or switch device manufacturers instructions. I believe it’s probably more on the permitted side rather than prohibited if I had to decide shooting from the hip, but I would closely scrutinize the workmanship, or “professional and skilled manner” of the terminations because of my experience. I would also need to know the device manufacturer’s position on it, as it may vary as to whether the configuration was included in the listing testing and evaluation. Probably not if it’s not clearly included as one of the alternative options in the wiring instructions. But I haven’t seen it prohibited in the instructions either, only in a couple online AI resources that didn’t pan out to actually be manufacturer sourced. So I wonder what testing would show, I’ve seen very old installations that looked fine, even with heavy use (mostly dwellings), and if it’s done well it probably is fine.
Same as pigtailing but without splices. Nothing wrong with doing that. Better circuit & lessens conductor count in the box.
I'd flame out after the first box trying to feed the romex back up through the load end of those pinch type plastic retainers.
Jap>
Absolutely, wouldn't even want to do it through a box with open holes and no clamps
Strip jacket first, fold over conductors, shove folded conductors into box hole? Never tried it but will if I get the opportunity.
Could even make the mid strips out in the open air and then shove it into the box already stripped, then just staple it down and terminate and done. Maybe?
Interesting for sure.
I could see it at the box locations on horizontal runs, but on up and overs or drops from above, I'd think you'd have to do the whole fold over thing at the bored hole in the top plates also.
Jap>