xptpcrewx
Power System Engineer
- Location
- Las Vegas, Nevada, USA
- Occupation
- Licensed Electrical Engineer, Licensed Electrical Contractor, Certified Master Electrician
I am dealing with a piece of equipment with aluminum load lugs "marked" but not necessarily "listed" for use with 12 AWG through 3/0 AWG conductors...
When applying 110.14(C)(1), what is the limiting temperature rating that should be used? (60 or 75 deg C?)
With the way the language is currently written 110.14(C)(1)(a) and 110.14(C)(1)(b) can both apply. For example:
110.14(C)(1)(a) applies because the termination provisions are marked for 14 AWG through 1 AWG.
110.14(C)(1)(b) applies because the termination provisions are marked for conductors larger than 1 AWG.
Please help me understand how the code handles this. Thanks in advance.
When applying 110.14(C)(1), what is the limiting temperature rating that should be used? (60 or 75 deg C?)
With the way the language is currently written 110.14(C)(1)(a) and 110.14(C)(1)(b) can both apply. For example:
110.14(C)(1)(a) applies because the termination provisions are marked for 14 AWG through 1 AWG.
110.14(C)(1)(b) applies because the termination provisions are marked for conductors larger than 1 AWG.
Please help me understand how the code handles this. Thanks in advance.