I was perusing (2020) 110.14(C), and I note that the second sentence of 110.14(C)(1) says "Unless the equipment is Listed and marked otherwise, conductor ampacities used in determining equipment termination provisions shall be based on Table 310.16 as appropriately modified by 310.12."
Table 310.16 Note 1 says "Section 310.15(B) shall be referenced for ampacity correction factors where the ambient temperature is other than 30°C (86°F)." Presumably any reference to Table 310.16 includes the Notes to the table.
So that means that ampacity correction for ambient temperature applies at terminations? This is contrary to my prior understanding, am I missing something?
I.e. if you have an outdoor 100A OCPD with 75C terminations, and the ambient temperature high is 104F, then a 0.88 correction factor applies, and the 75C termination ampacity of #3 Cu is only 88A. Meaning you'd need to use #2 Cu to get a termination ampacity of 101A, even with 90C conductor insulation.
Cheers, Wayne
Table 310.16 Note 1 says "Section 310.15(B) shall be referenced for ampacity correction factors where the ambient temperature is other than 30°C (86°F)." Presumably any reference to Table 310.16 includes the Notes to the table.
So that means that ampacity correction for ambient temperature applies at terminations? This is contrary to my prior understanding, am I missing something?
I.e. if you have an outdoor 100A OCPD with 75C terminations, and the ambient temperature high is 104F, then a 0.88 correction factor applies, and the 75C termination ampacity of #3 Cu is only 88A. Meaning you'd need to use #2 Cu to get a termination ampacity of 101A, even with 90C conductor insulation.
Cheers, Wayne