370.80 says we can use the free air ampacities of 310.15(B)(17) to size a feeder using cablebus (conductors on factory cable tray held apart with spacers). Since we would terminate in a SWBD, we would use the 75 deg column for ampacities.
110.14(C)(1) says unless the equipment is listed and marked otherwise conductor ampacities should be based on the regular 310.15(B)(16) conductors in raceway. The SWBD is not "listed and marked otherwise".
Any way around this other than putting an intermediate pull / splice section on both ends? The cablebus run is only about 50' and not worth the headache of a bunch of splices to go from 8 sets to 12 sets per phase.
110.14(C)(1) says unless the equipment is listed and marked otherwise conductor ampacities should be based on the regular 310.15(B)(16) conductors in raceway. The SWBD is not "listed and marked otherwise".
Any way around this other than putting an intermediate pull / splice section on both ends? The cablebus run is only about 50' and not worth the headache of a bunch of splices to go from 8 sets to 12 sets per phase.