Referring to 110.14(C)(1) that references Table 310.15(B)(16) for determining the allowable ampacities for terminations. If I understand correctly please confirm or clarify the following presumption:
If 500 kcmil is rated the maximum termination of 380 amp @ 75 deg C. If I install cable tray that allows me to rate the same cable at 620 amps 310.15(B)(17).
Q. Because of the cable tray and higher amperage ratting is it permissible to splice (2) 350 kcmil's and terminate to the 75 deg C connection?