I have an electrical panel and I've got 125A branch breakers rated for 60degC. I used #2 wire since next size up rule allows me to use that wire for the 125A breaker. NEC section 110.14(c)(1) seems to say that this is not allowed because since the terminal is rated for 60degC, I must use the 60degC rating of the wire, which is 95A for #2, meaning my wire is undersized. Is there any way around this?