I'm looking at 110.14(C)(2), Separate connector provisions.
I understand one place you might see this, is when you are bolting a crimp lug onto a busbar. Does this apply when that busbar is part of a manufactured product? Such as the secondary spades of a transformer or the busbar of a switchboard with bolt holes?
What are some other examples of where you can use this? I know about an otherwise-empty junction box, where you might install splices and taps, or even field-installed/mounted terminal blocks.
Separately installed pressure connectors shall be used with conductors at the ampacities not exceeding the ampacity of the listed and identified temperature rating of the connector
I understand one place you might see this, is when you are bolting a crimp lug onto a busbar. Does this apply when that busbar is part of a manufactured product? Such as the secondary spades of a transformer or the busbar of a switchboard with bolt holes?
What are some other examples of where you can use this? I know about an otherwise-empty junction box, where you might install splices and taps, or even field-installed/mounted terminal blocks.