Sean.Day72
Member
- Location
- Florida
I have a scenario where we are replacing VAV with heaters. The existing wiring is #12AWG. The kw load of the new heaters went up to 5KW @ 277 = 18Amp FLA for the new heaters. We are replacing existing 20Amp breakers with 25Amp breakers to accommodate this upsized load.
To save cost, are we able to utilize the existing #12AWG wire? I understand for loads under 100Amp to assume using the 60C ampacity table unless terminations are marked for 75C. The VAV has a label that says "Use wire suitable for at least 75C" that is not really stating the termination if rated for 75C. Has anyone ran into this? It is a lot of VAV units and could save a decent bit if existing #12AWG wire can be used vs installing new #10Awg to each new unit. Check the O&M and it does not state electrical termination temp ratings.
The Sqaure D circuit breaker is rated for 75C so good on that end of the circuit.
To save cost, are we able to utilize the existing #12AWG wire? I understand for loads under 100Amp to assume using the 60C ampacity table unless terminations are marked for 75C. The VAV has a label that says "Use wire suitable for at least 75C" that is not really stating the termination if rated for 75C. Has anyone ran into this? It is a lot of VAV units and could save a decent bit if existing #12AWG wire can be used vs installing new #10Awg to each new unit. Check the O&M and it does not state electrical termination temp ratings.
The Sqaure D circuit breaker is rated for 75C so good on that end of the circuit.