don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Unless the terminal is marked for other than 310.15(B)(16) ampacities, you are limited to those ampacities.
Unless the equipment is listed and marked otherwise, conductor ampacities used in determining equipment termination provisions shall be based on Table 310.15(B)(16) as appropriately modified by 310.15(B)(7).
The (B)(7) reference is to the reduced wire size permitted for dwelling unit service conductors.
 