joebell
Senior Member
- Location
- New Hampshire
Is this installation correct?
I need to provide a 60 amp circuit to a piece of lab equipment. According to 110.14(C)(1)(a) I need to size to these conductor so as not exceed the ampere rating of the 60 degree C column. I am installing conductors with type THHN insulation.
My question is if both the disconnect and the CB have a dual rating of 60/75 degree C is it permissable to use the 75 degree C column for the conductors ampere rating? That is how I am interpreting 110.14(C)(1)(a)(3) is this right?
Joe
I need to provide a 60 amp circuit to a piece of lab equipment. According to 110.14(C)(1)(a) I need to size to these conductor so as not exceed the ampere rating of the 60 degree C column. I am installing conductors with type THHN insulation.
My question is if both the disconnect and the CB have a dual rating of 60/75 degree C is it permissable to use the 75 degree C column for the conductors ampere rating? That is how I am interpreting 110.14(C)(1)(a)(3) is this right?
Joe