whip up on augie day ??

whip up on augie day ??

yes. but his general comment delt with using the 60 deg column.
I just wanted him to be familair wityh 334.80 brfore he "made his stand" and that was presented to him :)
If I were the "boss" and someone questioned me on using the 60 deg column, I'd go there to test his Coce knowledge.
 
spsnyder said:
I'm all for providing for future expansion and sizing conservatively, but No. 4 for a 20 amp circuit is a little excessive...:).

Most often the AC equipment is a combination-load and the manufacture must mark on the nameplate the minimum circuit ampacity and the maximum overcurrent protection device in keeping with 440-4(B), if so you use this information for the supply circuit.

Your case here is small enough it might be a room AC and then you need to comply with 422 and 440 VII
 
no its not nm cable, its all in emt. I just find it funny that my boss always cries poor but he oversizes alot of stuff that doesnt require it. I have a good grasp of vd drop so its rarely that.
 