So, I cannot use a 90C conductor on a 60C termination even though I use the ampacity of the wire at 60C?
So, I cannot use a 90C conductor on a 60C termination even though I use the ampacity of the wire at 60C?
Sure you can...See 110.14(C)(1)(a)(2)