You can use the 90? rating for derating purposed (fill, ambient, etc) so long as you use the 60? rating for the final termination when required.
(6 #6s THHN in a conduit, all current carrying.. 75amps @90? x 80% = 60, but IF your termination is limted to 60? the ampacity would be 55 amps)