Re: 110, 208, 240, AND 480
"Describe the reason for the proper connections for an electrical grounding system."
To use the NEC's definitions, as Roger posted, the answer would be:
It is to limit the voltage imposed on electrical equipment by lightning, line surges, or unintentional contact with higher-voltage lines and also to stabilize the voltage to earth during normal operation.
you guys mean the reason is not safety????
Not exactly. The goal of grounding is more to prevent lightning from striking electrical equipment, or to provide a path for the lightning should it strike.
A more compelling purpose of grounding is to provide a low resistance path to ground for line surges and unintentional contact with higher voltage lines.
For example, a typical utility voltage in residential neighborhoods is around 7200 volts.
Imagine a ground rod with 25 ohms resistance from the tip of the rod to the earth. 25 ohms is usually the benchmark for ground rod discussions, as the NEC states that a ground rod that has over 25 ohms resistance to ground be supplmented with one more ground rod (ultimate total of two rods, regardless of the resistance of the pair).
So this 25 ohm rod is driven in the earth, and you, being reckless and curious, connect it to an "ungrounded" (which is NEC parlance for what we commonly call "hot") source. Say it's a 20 amp breaker, with a 12 AWG wire running to the rod. What happens? Does it kick the breaker?
Electricity seeks
any path back to it's
source. (It doesn't seek the easiest path to ground, that's a myth.)
Since the transformer supplying the house is grounded, and the substation is grounded, and the power station is grounded, and the generator at the power plant is grounded, the earth is
a path back to the source. In this case, our source is the transformer just outside the house.
So when you hook up this 12 AWG wire to the ground rod, turn the breaker on, current is travelling from the breaker, through the wire, into the ground, and into the ground rod at the transformer. (Magically, we'll assume this rod has no resistance at all, for this example.)
Will the breaker kick?
No.
Ohm's law states that Volts = Amps x Resistance. When you solve for Amps (because we're wanting to know if enough amps are being drawn to kick our breaker), then it paints the picture:
Amps = Volts / Resistance
I = 120 / 25
I = 4.8
There are under 5 amps flowing on that wire, and through the rod. The breaker isn't even breaking a sweat, much less breaking the circuit because of the problem.
Now, from his truck, the utility guy is eating his lunch, musing over why this putz in the house is trying to kill himself by such a bizarre method, and decides to spice things up a bit. He walks over to the transformer, whips open the lid, and sends 7200 volts into the secondary side of the transformer, which was 120/240.
Now, how many amps are flowing through that 12 AWG wire and your rod?
7200 / 25 = 288 amps.
That ground rod is
much more effective at a higher voltage. Add to that the other grounding electrodes that are present at the house, and all the grounding electrodes connected to that transformer, and you'll have a lower resistance still.
So now, with all these electrodes pitching in, there's a shot that something the utility company owns is going to be receiving a massive amount of
fault current , and hopefully the event ends quickly.
That is grounding.
Bonding is a totally different concept.
Right now, the NEC unfortunately uses the term loosely, so you have to be careful of what you're dealing with when you read it and practice it. For example, an "Equipment Grounding Conductor" has absolutely nothing in the world to do with grounding at all, not one little bit.
Does this make sense to you? As kaskindm said, if the class you are taking does not adhere to this philosophy, drop it like a shot, they do not understand the difference. Mike Holt's Grounding vs. Bonding material is very informative, and as excellent for the beginner as for the seasoned. I'd highly recommend it.
And stick around here, there's several guys around here who're way sharper than I am on all this stuff.