Would it be considered a violation if due to reasons that could include not being comfortable with it or being uncertain about conductor sizes that the power company may choose to use, if someone marked a main panel board per 110.24, based on the infinite bus rating of the transformer Instead of calculating the resistance of the service wires?
If one were to do this, would they separately be required to do the calculation for the resistance of the wires to meet 110.16 V and ensure that the actual fault current is sufficient to trip the breaker in the clearing time on the label?